The voltage to ground of a high leg or stinger leg on a three-phase open delta system will be approximately?

Study for the ESCO Electrical Employment Ready Test. Prepare with practice questions, hints, and detailed explanations for each question. Get ready for your electrical certification exam!

Multiple Choice

The voltage to ground of a high leg or stinger leg on a three-phase open delta system will be approximately?

Explanation:
In a high-leg delta, the three line voltages are 240 V, and one winding is center-tapped to provide a neutral so two of the legs can deliver 120 V to neutral for standard 120/240 V service. The third leg, the “high leg,” does not center on that neutral. Its voltage to neutral is higher due to the phasor arrangement of the three phases; it ends up being about 240 V times the sine of 60 degrees, which equals roughly 208 V. So the voltage to ground on the high leg is approximately 208 V.

In a high-leg delta, the three line voltages are 240 V, and one winding is center-tapped to provide a neutral so two of the legs can deliver 120 V to neutral for standard 120/240 V service. The third leg, the “high leg,” does not center on that neutral. Its voltage to neutral is higher due to the phasor arrangement of the three phases; it ends up being about 240 V times the sine of 60 degrees, which equals roughly 208 V. So the voltage to ground on the high leg is approximately 208 V.